Domestic Electricians advice needed.

have an electric cooker to repair but the fault i believe is the house rather than the cooker.
The cooker is wired to a b40 40a circuit breaker.There is a 30a double socket near the cooker which is wired to a b32 circuit breaker.The house has overhead supply down through a big breaker to the distribution panel.When the cooker is on if you switch the kettle or toaster on the big breaker goes out.How can this be the socket and cooker are different circuits..Needless to say the kettle,toaster andcooker work fine individually.Its some kind collective thing.Any ideas welcome.





555

View User's Profile E-Mail User View All Posts By User U2U Member
daniel mason

posted on 17/6/14 at 06:20 PM Reply With Quote
By big breaker,do you mean RCD?






View User's Profile E-Mail User View All Posts By User U2U Member
JoelP

posted on 17/6/14 at 07:18 PM Reply With Quote
You really need a tester. I'll assume it must be an rcd tripping, because afaik normal main switches are just switches and don't measure current flow. The rcd could trip either due to a slight short between live and earth in the appliance, or a similar small leak between neutral and earth anywhere in the house - either another appliance that is plugged in, or on your fixed wiring. This would be difficult to locate via trial and error.





Beware! Bourettes is binfectious.

View User's Profile View All Posts By User U2U Member
big-vee-twin

posted on 17/6/14 at 09:44 PM Reply With Quote
You have an overhead supply called TT you will have an Earth leakage circuit breaker on the mains.

Anything with a heating element has a very small leakage current to earth quite normal and not dangerous as things get older the leak gets bigger.

If you have a few leaky appliances all on at the same time the ELCB will trip.

Yes its culumative.

Due to the earth leakage current and not an overload.

[Edited on 17/6/14 by big-vee-twin]





Duratec Engine is fitted, MS2 Extra V3 is assembled and tested, engine running, car now built. IVA passed 26/02/2016

http://www.triangleltd.com

View User's Profile View All Posts By User U2U Member

New Topic New Poll New Reply


go to top






Website design and SEO by Studio Montage

All content © 2001-16 LocostBuilders. Reproduction prohibited
Opinions expressed in public posts are those of the author and do not necessarily represent
the views of other users or any member of the LocostBuilders team.
Running XMB 1.8 Partagium [© 2002 XMB Group] on Apache under CentOS Linux
Founded, built and operated by ChrisW.