Macbeast
|
posted on 12/2/14 at 01:08 PM |
|
|
Electric Regs Advice Please
A friend has been told that she has to have her gas meter earthed. The meter is quite a long way from the distribution board. Would it be ok to run
the earth wire to the adjacent cooker outlet or to a convenient sink ( which is presumably earthed ) or does it have to be wired directly right back
to the Dis board ?
Also, what diameter of earth cable is required ?
I'm addicted to brake fluid, but I can stop anytime.
|
|
|
loggyboy
|
posted on 12/2/14 at 01:19 PM |
|
|
Arent they usualy earthed to the gas pipe itself with a strap?
http://www.diynot.com/forums/viewtopic.php?p=1641539
Mistral Motorsport
|
|
v8kid
|
posted on 12/2/14 at 01:21 PM |
|
|
the regs have changed on this but are not retrospective. All services have to be bonded together and to earth at the point of entry into the building.
used to be 6mm green/yellow sheathed I think its now 10mm and has been for a while. The gas meter also should be bonded across the inlet and outlet to
protect an employee changing the meter.
better wait until a qualified engineer comes on before you take this as verbatim though as its many moons since i did this.
Cheers1
You'd be surprised how quickly the sales people at B&Q try and assist you after ignoring you for the past 15 minutes when you try and start a
chainsaw
|
|
sparkyj83
|
posted on 12/2/14 at 01:21 PM |
|
|
bonding
Hi the gas requires a 10mm earth cable from the main consumer unit to within 300mm of the gas isolator with earth strap with warning tag
anything else just ask , Jay
|
|
slingshot2000
|
posted on 12/2/14 at 01:58 PM |
|
|
^^^^what he said, exactly correct!
|
|
Macbeast
|
posted on 12/2/14 at 02:26 PM |
|
|
Thanks chaps. Probably not what she wants to hear, but oh well
I'm addicted to brake fluid, but I can stop anytime.
|
|
sparkyj83
|
posted on 12/2/14 at 02:45 PM |
|
|
Your welcome. tbh it should not be hard hard of a job for a good sparky
|
|