House electrics question...
SierraL_killer - 26/10/09 at 08:33 PM

Hi,
Firstly apologies for the unrelated post but I know this place is full of knowledgable guys (and it saves me signing up to a different site just to ask one question!)...

Anyway, my flat has a lighting circuit protected by an RCD rated at 6A. I have just bought a new light fitting with four 50W halogen spots. The fitting instructions say:
A) "requires protection from a 5A fuse" - is the 6A RCD ok?
B) "fit new earth cable if there is not one present" - there isn't at the moment. Is this an issue?

The old fitting had 3 spotlights each rated at 60W to 100W if this helps.

Any comments are much obliged.

Cheers


SierraL_killer - 26/10/09 at 10:08 PM

Actually just found the earth (its just that the old fittting didnt use it so it had been tucked above ceiling rose)

Question A) still a concern though.


cliftyhanger - 27/10/09 at 12:28 PM

No problem, rcds don't come in 5A variety, 6 is std for lighting circuits.
The lights will draw 200w which is just under 1A, so the instructions are not really helpful at all. No surprise there.


omega 24 v6 - 27/10/09 at 12:36 PM

As long as the cabling is able to carry the required current then it should be fine.
(It should be at least the correct rating for the fuse box breaker especially if installed by a sparkie firm)


SierraL_killer - 27/10/09 at 04:43 PM

Thanks very much guys,

the new and existing wiring is fine.

Cheers,


Liam - 27/10/09 at 07:22 PM

I take it you mean MCB rather than RCD? Anyway, most important is the earthing. If the new light fitting says it requires earthing then it is class 1 and very much must be earthed unless you want to risk you, or anybody else, recieving a potentially fatal shock without warning when you change a bulb. The thing is, that previously unused earth may not be connected to anything at the other end either. Depending on the age of the installation/laziness of the electrician, a lack of earth in some or all of a lighting circuit is not uncommon. You really need to verify earth continuity from your fitting all the way back to the consumer unit/main earth terminal. Easily done with a multimeter and essential.

Liam