Hi all,
Time to ask for non car advice! The central heating and hot water have packed up (not a disaster as we've got an immersion heater and lots of
jumpers!). When the timer switches the CH and HW on, the boiler comes on for a few seconds, then switches off again. I've changed the boiler
thermostat, but no better.
Will call a professional tomorrow, unless the combined locosters have anything enlightening to say??
Ta
Chris
Depends on age it could be the thermocouple if it has one.
this isn't off topic, you wrote the topic! whatever you write is always going to be on topic!
what's your water pressure in the CH system like?
If its to low it will do what your describing
Open the filling loop for 30 seconds then close it and see if that clears the fault.
[Edited on 18-10-10 by mangogrooveworkshop]
does the heating work if you put it on constant?
my moneys on a stuck pump.
boiler lights gets to temp very quick due to no circulation then shuts down on high limit stat, either that or there is a air lock somewhere but
unlikely if its been running fine upto press.
have a look at the pump turn the boiler stat right down turn on both hw and ch then see if the pump is running free if not bash with hammer
Does HW work on its own ?
Not sure when you're system was installed but we had this a while ago on our 10 year old system.
Our tank is in an airing cupboard and had a temp switch on it so the HW got cut off when water reached temp regardless of how long you actually put
the water on for.
We must have caught the switch with clothes or something as it was turned right down so it never let the boiler fire for more than a few seconds.
That stopped central heating as well.
Hope yours is that simple
We also had a three way switch fail which as below shuts down boiler for no circulation.
Cheers all - it doesn't work on constant, but I'll try finding and then bashing the pump!
Ta
Chris
I have exactly the same problem. I have mate coming over tomorrow night to give me his verdict!
let me know how you get on good luck...
quote:
Originally posted by chrsgrain
Cheers all - it doesn't work on constant, but I'll try finding and then bashing the pump!
Ta
Chris
My monies on the boiler fan bearings if not pump. Assuming of course its a fan assisted boiler if not its as old as the hills. Check that the fan isnt
seized if it is youve got 2 options buy a new fan assy normally 100 squids or so or strip the bearings out nip down to your local bearing guy and
replace them for a tenner.
Let us know how you get on.
Cheers,
Bob
[Edited on 18/10/10 by splitrivet]
Well.... firstly thanks for all the help - a whack on the pump appeared to get it going, but the pump was noisy and getting very hot, so I replaced
that tonight (which was a bu^&er as the fittings had seized). Now the heating works on continuous, but not timed, and the hot water doesn't
work at all.
Any ideas??
Thanks again
Chris
could do with some more info what system is it y plan s plan also what boiler is it. Give me some more info and ill try to help.
rob