Central Heating Advice - Worcester Bosch 28i combi
Have a Worcester Bosch 28i boiler fitted in the loft 18 months ago.
It has started running with or without thermostat on.
Keeping the house at about 18 degrees.
I thought at 1st it was running because it was so cold outside that the frost stat was kicking in , but it is not that cold now and yet it still keeps
starting up for a while.
Any ideas?
[Edited on 2/1/09 by Surrey Dave]
|
|
|
daniel mason
|
posted on 2/1/09 at 01:51 PM |
|
|
your frost stat will set to around 5 degrees. It wil be still way below 5 degrees, turn the stat down as low as it will go eg -10 and see if it cuts
boiler out.
|
|
bob tatt
|
posted on 2/1/09 at 01:56 PM |
|
|
none adjusatble frost stat on the i juniors check temp in loft if not is it rf or hard wired stat. if its rf check the batteries in receiver.
|
|
Surrey Dave
|
posted on 2/1/09 at 02:07 PM |
|
|
What Temp?
Thanks , what temp is the internal frostat set to.
Is it worth wiring an external one?
Or do I just let it do its thing to protect itself .
I could open the loft hatch and let some warm air up.
Its my new ventilated upvc soffitts blowing a chill through the loft maybe.
|
|
JoelP
|
posted on 2/1/09 at 02:36 PM |
|
|
opening the loft hatch will only be a short term solution, it would cause condensation in the loft in the longer run. Maybe build a small insulated
enclosure round the boiler, to keep it warmer than the rest of the loft.
|
|
Surrey Dave
|
posted on 2/1/09 at 02:40 PM |
|
|
Sacred Bleu!!
Not another project!!
|
|
GasGasGas
|
posted on 2/1/09 at 04:54 PM |
|
|
Yep as above given the temperature lately its your vented loft causing the frost stat to kick in. Easiest remedy is to put a large kitchen cupboard
around the boiler to cut the draft down( check boiler litt for required clearances around it) and make sure all your pipes are well lagged!
Good luck
|
|