Author: Subject: Tripping a 16 amp circuit
HackleBear

posted on 21/10/14 at 07:46 PM Reply With Quote
Tripping a 16 amp circuit

I wonder if any one can help me, in my new workshop i am having issues with the MIG tripping the circuit breaker if the power is put above setting 3 out of six (trips on 4 +).

A little background information, the main supply comes from an independent 60A fused consumer unit, linked by 16mm2 cable to a "BG Garage Kit Enclosure 5-Module IP55 40A RCD Dual 6A & 32A MCB" the 6A & 32A MCB's have been replaced with a "BG MCB 16A C Type" this then leads to a "MK Commando Interlocked Angled Socket 2P+E 16A 200-250V (IP44)" connected by 2.5mm2 twin core cable(+earth).

The MIG is a new Snap-on PRO MIG 187 i believe it is 180A max output.

Any advice or hints as to the reason this machine may be tripping the circuit is greatly appreciated. also if you need any more information please feel free to ask. Thanks for reading.

View User's Profile View All Posts By User U2U Member
daniel mason

posted on 21/10/14 at 08:01 PM Reply With Quote
What load does the mig draw?
View User's Profile E-Mail User View All Posts By User U2U Member
HackleBear

posted on 21/10/14 at 08:35 PM Reply With Quote
the maximum current absorbed is 16A I belive
View User's Profile View All Posts By User U2U Member
daniel mason

posted on 21/10/14 at 08:52 PM Reply With Quote
Are you sure that's the case? I had a quick browse online and the 125amp mots needed 20 amps!
If the cable is 2.5mm you could uprate the 16amp mcb to a 20 amp type c. But without upgrading the supply to the mig then you can't go any higher!

View User's Profile E-Mail User View All Posts By User U2U Member
HackleBear

posted on 21/10/14 at 09:05 PM Reply With Quote
the instruction manual states that it is a maximum draw of 16A, i will get a 20A MCB and see if that sorts the issues out, thanks for the reply.
View User's Profile View All Posts By User U2U Member
MikeR

posted on 21/10/14 at 09:34 PM Reply With Quote
does it trip as soon as you pull the trigger or after a few seconds / 10's of seconds?
View User's Profile View All Posts By User U2U Member
HackleBear

posted on 21/10/14 at 09:52 PM Reply With Quote
The instance the trigger is pulled.
View User's Profile View All Posts By User U2U Member
HackleBear

posted on 21/10/14 at 10:18 PM Reply With Quote
I was double checking my instruction book and it appears to say the maximum absorbed current is 13A i believe i was wrong in previously stating 16A.







the images are taken from the instruction booklet.

View User's Profile View All Posts By User U2U Member
slingshot2000

posted on 21/10/14 at 10:57 PM Reply With Quote
Is it "tripping" the RCD or overloading the MCB ?
View User's Profile E-Mail User View All Posts By User U2U Member
HackleBear

posted on 21/10/14 at 11:13 PM Reply With Quote
The MCB, the RCD is fine.
View User's Profile View All Posts By User U2U Member
simonrh

posted on 22/10/14 at 07:41 AM Reply With Quote
Dont MCBs come in B,C and D type. Where B is suitable for basic resistive loads and D for big inductive loads or something similar with big in rush currents

Could it be that you need a D range with a bit more spark-up tolerance?

http://www.neweysonline.co.uk/MCBs/Static.raction

The d range ones are for big transformers which is ultimately what your welder is?

View User's Profile View All Posts By User U2U Member
omega 24 v6

posted on 22/10/14 at 11:41 AM Reply With Quote
Agreed high inrush currents at start up could trip a C type breaker. D types are much better at coping with this start up ( some folk call them motor rated breakers). But bear in mind the fault trip current is higher and the time taken to trip will be longer in an emergency/fault situation.





If it looks wrong it probably is wrong.

View User's Profile E-Mail User View All Posts By User U2U Member
daniel mason

posted on 22/10/14 at 11:47 AM Reply With Quote
Typically a B type will trip on overloads of 3-5 x rated current,
C type 5-10 x and D type 10-20 x over a set duration

View User's Profile E-Mail User View All Posts By User U2U Member

New Topic New Poll New Reply


go to top






Website design and SEO by Studio Montage

All content © 2001-16 LocostBuilders. Reproduction prohibited
Opinions expressed in public posts are those of the author and do not necessarily represent
the views of other users or any member of the LocostBuilders team.
Running XMB 1.8 Partagium [© 2002 XMB Group] on Apache under CentOS Linux
Founded, built and operated by ChrisW.