I have a air compressor which on the plate states 230 - 240v / 50hrz / 8amp and I believe it has a 1.75hp motor. I want to run this off a petrol
generator, what size generator do I need in Kv (ie 1 Kv 2.5Kv 8Kv etc etc.) Thanks Barry
|
|
|
Daddylonglegs
|
posted on 19/4/11 at 12:50 PM |
|
|
I would say at least a 2.2kw genny.
It looks like the Midget is winning at the moment......
|
|
Madinventions
|
posted on 19/4/11 at 12:51 PM |
|
|
240V x 8A = 1920W, so a 2KW generator will be running near to it's limit. (KV is kilovolts, KW is kilowatts. Power is measured in watts...)
I'd suggest a 3 to 4KW generator to be on the safe side.
As a secondary check, 1hp is approx 750W, so a 1.75hp motor consumes about 1.3KW. I'd still go for 3KW or more though!
Ed.
Mojo build diary: http://www.madinventions.co.uk
Solo music project: Syrrenfor http://www.reverbnation.com/syrrenfor
View my band website:
http://www.shadowlight.org.uk
http://www.eastangliankitcars.co.uk/
|
|
carpmart
|
posted on 19/4/11 at 01:10 PM |
|
|
Its not the steady state running that is an issue running a compressor off a genny, more the initially pull to kick it into action. Even quite small
compressors need a good lump of power from a genny to get them running!
You only live once - make the most of it!
Radical Clubsport, Kwaker motor
'94 MX5 MK1, 1.8
F10 M5 - 600bhp Daily Hack
Range Rover Sport - Wife's Car
Mercedes A class - Son's Car
|
|
big-vee-twin
|
posted on 19/4/11 at 02:07 PM |
|
|
240 x 8amps = 1940 va, then you need to take account of power factor which will be about 0.8
so 1940/0.8 = 2425 watts
then you need to take account of starting current.
Duratec Engine is fitted, MS2 Extra V3 is assembled and tested, engine running, car now built. IVA passed 26/02/2016