Im yet again looking at the heating system....
Im looking at fitting an Air source Heatpump, the manufacturor recomends fitting a "buffer tank" in the circuit to help maintain a more even
flow and to basically encourage the heatpump to run for longer rather than stopping and starting all the time...
Now my confusion starts.... Are they suggesting that the buffer tank is installed like a capacitor so the water from the heatpump flows through the
buffer on its way to the radiators..
Or, are they suggesting that the heatpump feeds the buffer and then returns to the pump and there is a seppreate loop inside the buffer tank to take
the heat away to the radiator system....
no its like a capacitor, they only have one port, with a diaphragm inside and a schrader valve on top to recharge them with air above diaphragm.
screwfix sell em pretty cheap
quote:
Originally posted by NS Dev
no its like a capacitor, they only have one port, with a diaphragm inside and a schrader valve on top to recharge them with air above diaphragm.
screwfix sell em pretty cheap
Yup, thats pretty much how I would do it...
But..If the heatpump is just heating the buffer tank, would you simply pump the water from the tank around the house, or run the central heating water
through a coil inside the buffer tank?
I guess its a case of suck it and see...the company who makes the heatpump sells various buffer tanks..Guess I have to buy one and see how best to
connect it up..
You could do it in a number of ways.
Is the heat pump designed to keep the tank hot most of the time? Is the heat pump just providing hot water for the radiators, or is it to be used for
domestic hot water too? What is the energy output from the heat pump? how many radiators are you running? what is the overall heat output for the
radiators in KW or BTU etc?
With a little more information we should be able to get to the best way to plumb your system with a correctly sized buffer tank.
[Edited on 25/9/07 by Digger Barnes]
I calculated the total heatloss of the house to be around 19Kw including hot water...
The heatpump I am looking at produces 24Kw at max, but will proberably average about 19Kw at very low temperatures...
Currently there is a sepperate imersion type hot water cylinder and a 17 radiator loop switched using a three port valve.....