posted on 22/1/18 at 10:42 AM |
|
|
Severed Main Ring
Like a foolish retarded idiot I have chopped into the main ring circuit and completely severed the cable. I was chopping out a socket and cable
wasn't exactly where I expected it to be. The cables are buried behind plasterboard and I have cut away the area to expose the offending cable.
I know the locost way is chocblocks wrapped in tape but I'd rather not.
Is there a small connector box that someone can recommend that can be perminately buried in the wall???
|
|
|
cliftyhanger
|
posted on 22/1/18 at 11:04 AM |
|
|
Wago's in a small box? But the electrician who did some re-wiring on a place I was recently working on used blue insulated connectors, the same
as often used on cars. Just crimped them up.Then wrote the certificate.....
I would prefer Wagos or a decent choc block (after all a choc bloc is the same system as used on every socket/switch in the house)
|
|
MikeR
|
posted on 22/1/18 at 11:14 AM |
|
|
I think Waco's are the preferred way and when I last looked at them supposed to be more reliable long term. But I'm no electrician ....
|
|
Irony
|
posted on 22/1/18 at 11:50 AM |
|
|
I think the safest option is to chop the cable out to the nearest socket and place another socket where the damage is. This will mean I will have a
bit of a random socket and I will have to chase a metre or so of cable. This is a bolt and braces option and will pass part P.
|
|
roadrunner
|
posted on 22/1/18 at 12:22 PM |
|
|
You need to have access to any threaded connections. If not, the push fit connectors wagos will be fine.
|
|
Mr Whippy
|
posted on 22/1/18 at 12:29 PM |
|
|
Personally I'd be fitting another socket (never know it might be handy for hovering etc) and joining it with that.
|
|
knight19770
|
posted on 22/1/18 at 12:34 PM |
|
|
I would suggest using through crimps as the best option if the joint is not accessible? I tell my sparkies only to use a junction box if we can get to
it afterwards. But best of all replace the broken leg of the cable, hopefully you can use the broken one as a draw wire.
|
|
stevebubs
|
posted on 22/1/18 at 03:01 PM |
|
|
I believe it has to be maintenance free if not accessible; sparkies will know better than me, but this may well be acceptable
https://www.amazon.co.uk/Ashley-J803-Maintenance-Terminal-Junction/dp/B00BATALJK
|
|
hearbear
|
posted on 22/1/18 at 08:37 PM |
|
|
The through crimps are what son uses and he is a sparkle or could you not fit a new box at the break
3.9Ltr SSC Stylus should be fun
|
|
nick205
|
posted on 23/1/18 at 10:19 AM |
|
|
No chance of fitting a socket at the break?
Once drilled though a mains cable buried in a wall (after realising I was still alive) I fitted a socket as a means of rejoining the cables (and
providing another mains socket).
|
|
dave r
|
posted on 25/1/18 at 08:12 PM |
|
|
Through crisps not that good on solid cores... solder heatsink in a box
I'd love to give my imaginary friend a great big hug,