posted on 17/9/15 at 10:23 AM |
|
|
a Question for the electricians
I think I have to earth bond my gas meter to the supply earth at the distribution box. What size cable do I need ? 2.5mm, 6mm ?
Also can sinks, etc be bonded to the nearest earth in a socket, or do they have to be run back to the dis board as well ?
I'm addicted to brake fluid, but I can stop anytime.
|
|
|
RedAvon
|
posted on 17/9/15 at 12:18 PM |
|
|
My understanding is below, however I am happy to be corrected.
10mm2 earth cable connected within 600mm of incoming supply direct to distribution board.
If you have RCDs in the consumer unit there is no longer a requirement to earth bond sinks/rads etc.
Hope that helps
Ian
Bricoleur
|
|
ian locostzx9rc2
|
posted on 17/9/15 at 12:59 PM |
|
|
We had a new consumer unit fitted and had to have a new 10 mm earthing cable because of new regs .
|
|
daniel mason
|
posted on 17/9/15 at 01:59 PM |
|
|
10mm cpc to incoming services. If you run it into gas box there will usually be enough room to get an earth Clamp on the pipe
|
|
Macbeast
|
posted on 18/9/15 at 09:00 PM |
|
|
Fine chaps. 10mm it is then. Thanks.